can you explain why neutrals and ground are ok at the main panel but not ok in the sub panel?
I keep wanting to revisit this for some reason. It's a great question and I don't think I've explained it very well at all.
Any time you have neutral and grounds terminated to the same busbar, the panel in question has to be fed with SEU, or in other words, the neutral doubles up as a grounding conductor as well. Inaccurate statement but will have to do I guess.
The job of a neutral conductor is to carry the return current back to the source, as I've stated, but it's important to know that the neutral carries the imbalance of the load.
Say, in my main panel fed with SEU, One incoming hot leg (or phase) is drawing 60 amp. The other hot leg is drawing 40amp. This current draw is being utilized by your branch circuits feeding your entire house.
The return current traveling back to the transformer is not 100 amp. It's 20 amp. This is why neutrals are allowed to be smaller than the hots in some instances. This is why it's good to balance the loads in your panel also. If you know 2 appliances are likely to be running at the same time, then put them on opposite legs. On the other hand, you would put a separate AC unit and furnace on the same leg because you know they'll never be running at the same time.
Kitchens are required to have 2 - 20A small appliance branch circuits. I generally stab them onto different legs.
The same holds true when using Multi Wire Branch Circuits (Using a 14/3 to feed two separate 120v loads but sharing the neutral). If both 120v loads are drawing 10A, then the return current on the shared neutral will be 0.
So anyway, the grounded conductor (neutral) of your SEU Main Service Cable should never see a "full" load.
EDIT:
The arrangement of the hot bus bars is naturally set up to stagger but you can unbalance your panel easily if you don't think about what goes where before hand.
Say you run a sub-panel for your grow room and you choose to start attaching breakers down the left side of the panel. This is the arrangement you happen to put the breakers in (on the left hand side only)
20A Single pole - 1000w dedicated ballast for bloom - Phase A (L1) or "leg" as I call them
15A Single pole - Ceiling light fixture to throw a green CFL into - Phase B (L2)
20A Single pole - 1000w dedicated ballast for bloom - Phase A
15A Single pole - dedicated water and air pumps for reservoir. - Phase B
15A Single pole - dedicated 600w for grow - Phase A
You've got a seriously imbalanced panel there. As long as you sized the feeder cable appropriately, there still not really an issue but it's bad planning to arrange breakers like that. You should have done:
20A Single pole - 1000w dedicated ballast for bloom - Phase A
20A Single pole - 1000w dedicated ballast for bloom - Phase B
15A Single pole - Ceiling light fixture to throw a green CFL into - Phase A
15A Single pole - dedicated water and air pumps for reservoir. - Phase B
15A Single pole - dedicated 600w for grow - Phase A
Study the empty hot busbars on a de-energized panel and you'll see how they are staggered.