No 240, just want to split it into 2 120 circuits.
I've read through the entire thread, and found it extremely helpful. I have concerns though about my "main" panel, as it does not have a main disconnect, as well as the issue with the 10-30 not having a separate ground and neutral. Obviously, the 12/2 will need to be replaced (thanks for that info), so I guess I might as well just re-run a 10/3 from the 30amp breaker (I will need a separate ground and neutral, right?) to my mini-sub-panel (spa breaker- can it even be used in this application?). This would eliminate the 10-30R, and could just be run through the wall.
Anyway, don't want anyone to think I haven't read (and absorbed at least some) as much as I can, I just have a few specific questions, and don't want to risk burning down a rental that I share with other folks.
Thanks in advance for any advice.
Just to be clear, I didn't intend to imply in any way that you hadn't read the thread. I'm just trying to lighten MP's workload a tiny bit by answering any questions that I'm 100% sure I know the answer to.
How far is it from your main panel to your grow room where you'll be installing the outlets? You might consider forgetting the sub panel idea altogether. You are going to need to run a new 10/2 anyway to feed the panel, so you could just run another 12/2 (or 14/2 if you only need 15 amps) and install two 20 amp breakers into your main panel slots instead of one DP 30 amp.