so i will not have 100a running to my 100a indoor sub-panel or will i?
No, you will not. Only if you use a 100A double pole breaker back in your main panel will you have 100A. But if you put a 100A breaker on #6 wire, then I wish you all the luck in the world. Please see below. I'm starting to feel like a broken record.
madpenguin said:If you wanted the full 100A for that MBP in your grow, then you needed to use #2 copper or 1/0 aluminum fed by a 100A double pole breaker in the main panel.
jyme said:so i need to go buy new wire again that sucks copper is high?
If you want a full 100A, then yes. You need to get 1/0 AL SER and feed it with a 100A DP breaker in your main.
jyme said:and then will i still need the 60a dp or can i double tap it?
If you go buy 1/0 AL SER, then no, you don't have to use the 60A DP breaker unless you want to limit yourself to 60A but if that was the case, then why go out and buy 1/0 cable thats rated for 100A?
And no, never double tap anything as a general rule. Some stuff is made to be safe when double tapped, such as a QO breaker. Very few lugs are rated for 2 wires. One of those wires won't make good contact and then you've got a hot spot because of increased resistance.
Always feed subpanels with a double pole breaker back in the main panel. I did an extensive tutorial about this on pages 3 and 5 I believe. Dude, please read before you start wasting your time (and mine).... Not trying to be a dick, I'm really not, but I've repeated the same stuff 3 times over the last page. Not only that, the main information has already been gone over in this thread. Take the time to read it and you might learn a thing or two.