OK. Here are the numbers. A lot of this isn't currently running, but are foreseable additions at some point.
Flower room: (2) 1k hps. SS-1. I haven't checked the actual
numbers for these yet.
(2) inline fans. 228w each
(2) oscillating fans. 47w each
Veg room (2) 1k mh. SS-1.
(2) inline fans. 228w each
(2) oscillating fans. 47w each
Missing voltage in there. You need 2 variables to arrive at the third. I'm sure you've posted it earlier. Did you already have 240v cords and they were multi-tap ballasts? You wanted to run all 3 lights at 240v, or were you still undecided?
Yea, it sounds like it. If your right next to the panel and it's an unfinished basement plus you have free breaker slots then don't fuck with the supersized 240v/120v combo circuit. No need for it unless there was a good bit of distance involved.I think I am making this harder than it needs to be.
You can run oversized wire for a circuit. In fact, you need to in certain instances, none of which really apply to you. If your ballasts currently run at 120v and you have to buy the cords to make them run at 240v, then I wouldn't fuck with that.
I'd run them at 120v and use a 12/3 multiwire branch circuit attached to a double pole 20A breaker for the the flower room. Use a double gang metal box to affix to the wall. Buy some spec grade 20A receptacles. They are still 120v receptacles but have a little horizontal slot on one of the prong inserts. Cost about 2.49 a piece or something like that. Put the red wire to one receptacle, put the black wire to another separate receptacle. Cut 2 pieces of white conductor at 6 inches a piece and twist them together to the neutral coming from the panel with a pair on linemans pliers. Then wire nut them really good with a red wire nut. One white pigtail to one receptacle, then the other white pigtail to the other receptacle.
That's a multiwire branch circuit. You'll be drawing 10A on both the red and black conductors at 120v. That means the neutral will be carrying 0 amps worth of current back to the panel. It pretty much works like a 240v circuit. If you had 8A on the red wire and 10A on the black wire, then the neutral going back to the panel would be carrying 2A worth of current.
Then run another 20A 12/2 circuit to the veg room. That'll be just a plain old 120v 2 wire circuit. That will leave you room to spare and the wire will stay nice and cool at 10A per leg.
Just my 2 cents anyway. Maybe 25' of 12/3, 25' of 12/2, a single pole 20A breaker, a double pole 20A breaker, a single gang metal handy box with metal receptacle cover, and a double gang metal box with a double receptacle cover. Get some EMT or the gray electrical conduit and some conduit straps and masonry screws and a masonry drill bit a tad smaller than the screws and your in bussiness. Some wire staples. A hammer. A proper pair of wire strippers that will evenly cut the sheath off the cable. Some green grounding screws. White wire nuts. Red wirenuts. 2 NM connectors for the knockouts at the top of your panel.... A 3/4" auger or paddle/spade bit and a drill to run the wire thru your ceiling/floor joists drilled dead center from top to bottom of the joist.
That's about it.. You've really got about the easiest setup to do. Way easier than most of us had to go thru in order to get our grow room running.