Never heard of them, but will check them out.
Thanks,
BG
Thanks,
BG
cocktail frank said:pharma can has given sound advice in the past around this forum, id listen to him too.
clowntown said:Even an armored 10/2 flexible metal cable w/ standard insulation on the ground wire is not up to code for a 220/240v outlet, or just the 10/2 Romex without real insulation on the ground?
If not up to code for both NM and flex. metal, what is the reasoning behind this? In other words, what could possibly go wrong by using 10/2 for 220/240v? Both in a typical / practical scenario, and also in theoretical / rare situations? What is a 10/2 NM (without insulated ground) typically used for, that is up-to-code?
[Apologies for the extreme noobishness; just a few weeks ago I didn't even have the slightest clue on what exactly a 220/240v involved... didn't know that it was two hot legs, didn't know diddly squat.]
LOL...I thought that was good info and definitely another piece of the puzzle. What that brought up for me was a probably bigger issue is when people do longer runs of wire and don't maybe kick up to the next gauge.luciano28 said:Oh and with the correction factors I totally agree with you guys 00420 and Whatever, I was overthinking it a bit because the wire in a grow room is never gonna be huge enough to require a larger gauge wire because of the heat, now in our furnace room where we have busses and 1/0 wire running and it gets up to 120 degrees on a hot summer day its different and heat make a much bigger difference to the amperage rating. Not so much on relatively small wire like 10 and 8 gauge wire.
I get high too much, lol.
cocktail frank said:this whole thread makes me LOL.
everything i said in my first post is still gold and true.
i am a licensed electrician and been doing this shit since '95.
as far a correction factors for temp, you have to go w/ the lowest temp rating of w/e you used to wire the grow.
wether it be the temp rating of the wire, or the breaker.
yes, they all have temp ratings right on them, they are thewre for a reason.
as far as the sub coming out of another sub, not a great idea.
subs should only come out of main panels, as good practice.
if i read it correctly, you have a 60a sub coming from the main, then a 40a sub coming from the 60a sub?
wow, not cool.
DH, you can waste your money replacing the breaker if you please.
dont heed the advice you have been given.
00420 seems to know what he is talking about.
pharma can has given sound advice in the past around this forum, id listen to him too.
luciano seems to be up and coming.
maybe if your lucky, you could actually purchase a defective breaker as a replacement.
then, just maybe, it wont trip , LIKE IT SHOULD W/ UR SETUP, then a fire will erupt.
you obviously want to do whatever you want to do, so good luck w/ it.
this is why i dont chime in on electrical questions like i used too.
nobody listens and ive typed all this info over and over all over this subforum.
i even started a electrical safety thread to help folks out.
i advise you thumb thru it. this goes for everybody.
nothing lands you in jail faster than an electrical fire in yer grow.
ill have it on here monday..JamesChong said:Hey DiggitalHippy,
These unit call for hard wiring into a panel, "But" and I say but. Depending on the unit you get. One, I think the 4 lamp unit. Is a 30 amp unit and you can install a dryer cord and plug into a dryer outlet. That's if you have one that your not using. That's what I'm thinking about doing. The other unit, being the 8 light unit. It is a 40 amp unit. If you have a spare or unused 50 amp ranger outlet. You could install a 50 amp range cord to the unit and use it, but I would change out the 50 amp breaker with a smaller 40 amp break. Not to over load the CAP unit.
I'm buying the 8 light unit with dual trips next month. I'm going to run 2 4x8 growboxes with either 2400 HPS or 1800HPS per a unit and run half during the day and the other half at night. So, I'll only be running half the load on the unit. Trying not to run all 3600-4800 watts at one time. I'm also going to run a brand new line to the box to be save also. I don't want to have any fires at all and know the wiring and breaker is right.
Good luck with your unit. Make sure to share the install pictures with us.
Later,
BG
DIGITALHIPPY said:its a 80/80 breaker on the main to sub1
and will be a 60/60 breaker from panel1->panel2
...
00420- if i have people up in here to investigatin my 'code' problems i think im going to have other problems....
00420 said:80% of 80 = 64
80% of 60 = 48
that leave's you 16amp's on sub 1 if 80% is used on sub 2
you all so said you had #6wire on sub 1 from main witch is a 65 amp max ( i would not go over 60) and now your saying it's a 80/80 breaker on that line.....
be careful here DH
2 line's 64 amp's each line
-30 for light's (6k)
line 1 64-30=34
line 2 64-30=34
-15 for a/c (120v)
-9 for dehu (120v)
line 1 34-15=19
line 2 34-9=25
if your truly running #6 on sub 1 that would be 16 amp's less to my math
line 1 19-16=3
line 2 25-16=9
i know your running fans pumps veg/clone light's ect....... most fans are .7-3 amp's
"code problems" are just prob's on top of prob's
00420 said:"code problems" are just prob's on top of prob's