JamesChong said:Sorry, hate to butt in. Since we are on the subject.
00420, you think it would be safe for me to run one of these units on a 30 amp dryer outlet? Planning on running 4 x 600HPS during the day and the same at night. So, I would be running 4800 watts, but half at a time. Don't want to burn my place to the ground.
Killer thread with lots of info. Thanks for sharing everyone. Have a nice weekend all.
Later,
BG
00420 said:sry homie but i dont even know wtf that is.... hahaha
i do know 4 x 600 = 2400/240v=10amp's and if you put that on a 30amp line it should run 24/7 like you are asking.... but then again you could have crusted dryr wire from the 50's
edit: more then likely you will be running at 220v + line voltage drop so more like 12-13 amp's
yes it is..... that slipped my mind and was thinking 2 #10's would work but not be to code....luciano28 said:That table is probably the most important page of the whole book.
JamesChong said:It's a 8 light unit that has two triggers. You have a timer for one side and another timer for the other side. Kind of like a flip flop but with all 8 ballast and not 4. I can split up the 8 lights. To run half the light during the day and the other half at night. Less amp draw and less of a high wattage pattern if the light company is watching with software.
What's this wire from the 50's? If I got to, I'll just run a new wire. Since the wire is close to the box.
Thanks,
BG
LOL...I'm in over my head here but do understand the 10/2 and 10/3 thing. To be safe ran 2000 watts on a 240 dryer circuit like 8PM to 8AM my first indoor...and clothes were done only during the reverse. I was fortunate in that the house had 50's 2 conductor to the sockets but the dryer and hot tub circuits had 'fresh' lines coming from the main panel at the meter. I actually tapped off that dryer circuit and also ran the vent fans during lights on.00420 said:DH one other thing i just noticed your using 10/2 not 10/3
10/3 is round you have flat that mean's your common is a bare wire thats not really a good idea my friend you have short run's and it would be really easy to fix cheap...
I think I know enough to say if temp correction factors come into play you were running too close to the edge to begin with and didn't leave enough wiggle room.luciano28 said:00420 do you think the correction factors for temperature should be used when wiring a grow room?
What's the big deal with running 10-2? If it was 10-3 he'd have to cap the neutral. All the NEMA 6-20s I've seen are 3 wire self-grounding. Are we talking about future-proofing or what?00420 said:DH one other thing i just noticed your using 10/2 not 10/3
10/3 is round you have flat that mean's your common is a bare wire thats not really a good idea my friend you have short run's and it would be really easy to fix cheap...
Even_Steven said:What's the big deal with running 10-2? If it was 10-3 he'd have to cap the neutral. All the NEMA 6-20s I've seen are 3 wire self-grounding. Are we talking about future-proofing or what?
i was to tell i started growing......Whatever said:Thanx OO420 as I've learned a bit more here...definitely a wiring dweeb.
honestly bro i have no clue...but my guess this is why we stay at 80% load i can say for 10yr's now i have never had a prob with 10/3 with 4k if i do a room with 4k+ i run a 2nd set or wire & split the load i hope this helps you ...haha the max i would say is 90 anything after that and your plants start to look like shit.... BUT a lot of wiring is in the wall's or out of the grow room where i have seen it up to 115luciano28 said:00420 do you think the correction factors for temperature should be used when wiring a grow room? I mean I hope everyone keeps their temps under 30C(86F), that is what the table is based on, up to 30F, but we all know things can happen and people should be prepared for it when wiring. What do you think the max temp a grow room could get to? Without it being on fire, lol. I know in our furnace room at the mill we have wire 2 sizes too big for the overcurrent device(fuses and breakers are OCD's) because of the ambient heat. There are correction factors for the amperage rating of each gauge wire according to the ambient temperature.
agreewhatever said:I think I know enough to say if temp correction factors come into play you were running too close to the edge to begin with and didn't leave enough wiggle room.
Even_Steven said:What's the big deal with running 10-2? If it was 10-3 he'd have to cap the neutral. All the NEMA 6-20s I've seen are 3 wire self-grounding. Are we talking about future-proofing or what?
luciano28 said:I think if I understand right he is running on 220v so he is using the wire that was meant for the common as a hot and the bare wire meant for grounding as his common. Trainwreck waiting to happen. 10-2(3wires, 2 insulated) 10-3(4wires, 3 insulated)
luciano28 said:P/E=I
P=Watts
E=Volts
I=Amps
1000w/240v=4.17amp
Now multiply that by 5=breaker pops.
Thats all it boils down to, he doesnt have 40 amps, he has 20 amps(really he only has 16, breakers will pop at 80% of their rating)) and he is exceeding that everytime. The breaker is working just fine.
It says "20" on it for a reason.
I think it's setup that way to handle the heat that comes with the extra watts of 240v.PharmaCan said:Interesting. So riddle me this, smart-ass. How come you can take the connecting clip off the knobs on that breaker and have two 20 amp breakers, or why you can put a clip on two 20 amp breakers and get a 240v breaker? Each side of that breaker is 20 amps. 1/2 your current is passing through one breaker, the other half is passing through the other breaker.
Breakers don't pop at 80% of their rating, it is recommended not to exceed 80% of their rating because of surges and such.
PC