T
Teeg420
The instructions for the mlc 8 say to use a 40 amp breaker. Does that sound right? I know you never want to exceed 80% of the breakers capacity. Im using 1kw ballast, so 4.5 to 4.7 amps multiplied by 8 equals 36 to 37.6 and a 40 amp breaker at 80% of its load rate is 32 amps. So im confused are the cap instructions wrong? I don't want to start a fire. thanks.