DocTroll, where've you been? It looks like another cut & paste job from you since it is readable, but as usual, your advice is wrong.
First, per the NEC, you are limited to 80% of the circuit's breaker rating for continuous loads which are any loads of greater than 3 hours duration. There are specially-listed breakers available for 100% duty on continuous loads, but they are expensive and very hard to find.
Second, a 3-wire 240v circuit is (2) hot legs of 120v and a GROUND, not a neutral. Only a 4-wire 240v circuit can be safely used to split off 120v circuits because it has both a neutral and a ground.
Third, the CAP controller is junk. They didn't have either UL or CSA approvals, didn't use proper fusing, had inadequate wire sizing, the receptacles are Chinese-made crap, and they are out of business.
Nvarma, the problem with what you are doing is that you have a 30 amp circuit that you are trying to run 20a components on. There needs to be some intermediate protection installed to limit the current if (when) something goes wrong. With the exception of the 125v receptacle your list is ok, but you need some additional equipment. You can add a small sub-panel to your installation and it will work fine - use the dryer cord to feed a 240v sub-panel, and set a double-pole 15 or 20a breaker in the sub. You can then feed the T104 with 12/2, and use it to power a receptacle. The receptacle should be changed out with either a NEMA 6-15 or 6-20 design (15 or 20a, 240v).
First, per the NEC, you are limited to 80% of the circuit's breaker rating for continuous loads which are any loads of greater than 3 hours duration. There are specially-listed breakers available for 100% duty on continuous loads, but they are expensive and very hard to find.
Second, a 3-wire 240v circuit is (2) hot legs of 120v and a GROUND, not a neutral. Only a 4-wire 240v circuit can be safely used to split off 120v circuits because it has both a neutral and a ground.
Third, the CAP controller is junk. They didn't have either UL or CSA approvals, didn't use proper fusing, had inadequate wire sizing, the receptacles are Chinese-made crap, and they are out of business.
Nvarma, the problem with what you are doing is that you have a 30 amp circuit that you are trying to run 20a components on. There needs to be some intermediate protection installed to limit the current if (when) something goes wrong. With the exception of the 125v receptacle your list is ok, but you need some additional equipment. You can add a small sub-panel to your installation and it will work fine - use the dryer cord to feed a 240v sub-panel, and set a double-pole 15 or 20a breaker in the sub. You can then feed the T104 with 12/2, and use it to power a receptacle. The receptacle should be changed out with either a NEMA 6-15 or 6-20 design (15 or 20a, 240v).