the space i'm in currently has a 240 50 amp service coming into it. i thought it was perfect for my 8 light controller. however, the gauge of wire being used is 11. so given the gauge, i only really have around max 4000 watts to use even if the breaker is 50 amps? correct?
i realize i need to replace the wire with gauge 6 or 8 at least if i want to draw more power. the problem is i do not have access to the main breaker switch. i have access to the 50 amp breaker and the rest of the breakers in the space, but i do not have access to the central breaker and therefore cannot kill all power.
is there a way to rewire without turning off central breaker safely? i know you can extend the circuit, splicing two wires together, by just turning off the breaker of the circuit you're working on? but when you rewire from the breaker box is it completely necessary for power to off completely?
You must have a typo - there is no 11 gauge wire. If you meant 10, it is only rated for 30 amps and needs to be changed asap. 8 is good for 40 amps, and 6 for 60.
If you work carefully, there should not be a need to kill the power to the whole panel. You can turn off the 50 amp breaker, remove the existing wire, and replace it with a larger conductor. Make sure that you don't brush up against anything that is still energized, or shut off the other breakers in the panel and the only thing that will still be hot are the busses and the main lugs. A technique used by electricians when doing hot work is to keep your left hand in your pocket and only use your right. If you get hit, this helps keep the current from flowing through your heart. Also, a pair of new, clean (so they don't have conductive material imbedded in them), snug-fitting leather driver's gloves are a good insulator.