Everyone else is getting in on this so I guess I will too. Cam, so far about the only thing I see that you have right is the fact that it is alright to undersize the breaker. The purpose of a circuit breaker is to protect the wire that feeds the load (your ballasts). If your protect 40amp wire with a 30amp breaker it is just fine and NOT a code violation. Heat is generated by excess current or a fault, not being there it is difficult to know which one is your problem. A couple of questions for you.
1. Is this a new setup or have you used these parts before? If you have used the ballasts before with no problems it would indicate it’s not a load issue.
2. Do your circuit breakers screw into the busbar or snap in? If they screw in one may be cross threaded and the breaker may not be tight against the busbar. I have seen them glow red hot from that.
3. Did you bring a neutral and a ground to the sub-panel? If yes are the neutral and ground wire tied together at the sub-panel? They shouldn’t be.
4. There should be no load present on the neutral when all the lights are working.
5. did you take a separate black and white for each circuit or did you “share” a neutral between 2 circuits. If sharing try not sharing neutrals. Did you check to see if the neutral or ground wires are hot?
Anyway those are some things that can create heat issues. You say the wires are not hot, only the breakers. I would really start by looking at neutral and ground issues, as well as tight connections.
With respect to the electrician who suggested you buy a bigger breaker, you may suggest he get a diff career.
Keep us posted
1. Is this a new setup or have you used these parts before? If you have used the ballasts before with no problems it would indicate it’s not a load issue.
2. Do your circuit breakers screw into the busbar or snap in? If they screw in one may be cross threaded and the breaker may not be tight against the busbar. I have seen them glow red hot from that.
3. Did you bring a neutral and a ground to the sub-panel? If yes are the neutral and ground wire tied together at the sub-panel? They shouldn’t be.
4. There should be no load present on the neutral when all the lights are working.
5. did you take a separate black and white for each circuit or did you “share” a neutral between 2 circuits. If sharing try not sharing neutrals. Did you check to see if the neutral or ground wires are hot?
Anyway those are some things that can create heat issues. You say the wires are not hot, only the breakers. I would really start by looking at neutral and ground issues, as well as tight connections.
With respect to the electrician who suggested you buy a bigger breaker, you may suggest he get a diff career.
Keep us posted