Me thinks you need to reread his last post. Are you a tech? If so how did you learn? Also this unit is designed to work in low temps. Doy you know how a hot gas bypass valve works ?I think the last thing any qualified Air conditioning service man should be sugessting a layman do is check the refigerant charge or operating pressures. Especially when all other posibilities have not been ruled out.
Most likely the problem is not a loss of refrigerant.
We have verified that the indoor fan is operating, that the filter and evaporator coil are clean. So We are assuming it is not a reduced airflow across the evap coil problem.
He has stated several times that it all started when the temperature outside cooled off.
He as said the unit displays an outdoor temperature of 47* F.
Now the way i think this unit works, is it pulls room air over the condenser coil, and not outdoor air, but I suppose it could be ducted to pull outdoor air over the condenser coil.
But I do know that if the air blowing across the condenser coil is only 47* F, a low head pressure will result and with out controls to regulate the head pressure, in proper operating range, that the ultimate result will be an iced over evaporator coil after several hours of use.