Wow, okay, thanks. WAY over my head, I'd have an electrician do it before I took the risk. I don't trust myself. Thanks again!Whether the dryer circuit works depends on the circuit arrangement. The 3-wire 240v mentioned above will actually have 4 wires total at the receptacle - there is also the ground to account for. If there are only 3 wires in the receptacle, then a neutral is not present - just 2 hot legs and a ground.
If 120v is all that you need, then the receptacle wiring could be re-arranged even if it is straight 240v by moving one of the hot wires from the breaker to the neutral buss. Of course, if it is a 4-wire style then it would be usable "as is" by using only single-pole breakers in your cord-connected subpanel.
Be aware that if a hot wire is converted over to a neutral, white "phase tape" should be used on the wire at each end to mark that it has been converted to that purpose. Also, the receptacle should be changed over to a Nema 5-30 configuration so that a 240v appliance cannot be plugged into it.
The timer would not be needed, but some downstream circuit protection is required if the downstream components are the usual 15a variety.