Ok, I had some time to work on this this today. Had a couple hiccups but nothing worth mentioning. I decided to run the wire in conduit...
View Image
View Image
View Image
Does the water heater timer step down the voltage at the same time? It looks like a 240v dryer plug going into the timer and 120v panel.
I'm having trouble reconciling the 50 amp breaker feeding all this.
The outlet is 30 amp, the dryer plug 30 amp. The load side of the timer is orange romex (30 amp) feeding a sub with no main breaker.
The breaker in your house panel feeding all this is the only overcurrent protection you have. Meaning it must be a 30 amp breaker, and not 50 regardless of whatever plug rating it is attached to.
I have a dryer outlet I would love to use but only for 120v. Do I need the timer or can I just wire outlets thru a panel and dryer plug?If you carry 3-wire 240v (2 hot legs and 1 neutral) through the timer and into the sub-panel, then both 120v and 240v are available at the the sub. The neutral is unswitched, and if you go from either hot leg to neutral, you get 120v. If you go from hot to hot, you get 240v.