I SHOULD MENTION:
When I first released refrigerant into the system by opening stem valve, I had a blast of pressure come out the low side flare nut because I apparently didn't tighten the flare nut enough. I quickly closed the valve and took a wrench to the flare nut immediately before too much refrigerant could leak out. I was surprised the AC worked for 24 hours ice cold before crapping out. This tells me I didn't leak all my refrigerant out with that initial release? But maybe the leak could be at the low side flare nut outside and I plan to use nitrogen to verify. You can see what looks like a wet spot under the low side ports. I think the r410a stained the concrete from when the refrigerant blasted out the flare nut from 5 nights ago?
wet spot it probably oil.
keep in mind r410 is a mixture of refrigerants with different boiling points.
when you leak vapor you typically leak more of one refrigerant than the other causing the ratio of r32, r125 etc to change.
basically when you leak vapor, you need to recover the charge and weigh in a new charge.
put your gauges on the unit and see if there is any pressure.
if you have any pressure, do a fast leak check with some soapy water.
the leak is probably at a flare nut. this is where probably 95% of minisplit leaks are at.
find the bad flare, cut it off and reflare the copper with a decent flaring tool. hilmore makes a good one.
while you are at it, cut off all that fucking extra lineset length. what is that bullshit?
alternately you can just swage and braze or even soft solder the connection.
if you dont find any leaks with what little pressure is left... recover the charge and pressurize it with nitrogen and do the leak check again.
do not vent the remaining charge of refrigerant. recover it with a proper machine.
only shit bags vent to atmosphere.