setting up a 6kw room.
If I have a 150 amp panel that say, needs a #3 wire to feed it
and I have plenty of #6,
can i double up on #6 and safely carry the load?
I agree with rives. you may use #1 Cu or #2/0 Al for a 150A service between the meter and the main breaker per Table 310-15(b)(6)..
FYI ,
THWN stands for "Thermoplastic High Water-resistant Nylon-coated." THWN is a designation for a specific insulation material,...
Sorry, I worded that poorly. What I meant was that 150 amps is a hell of a lot of extra power for a 6kw grow. At 25 amps for the lighting, I would think that you could probably fit that plus all of your auxiliary equipment on a 60 amp panel if necessary. If you size your breaker to your existing wire, it sounds like you could easily run a 100 or 125 supply, have lots of room for future expansion and avoid the cost of larger conductors.
Sorry, I worded that poorly. What I meant was that 150 amps is a hell of a lot of extra power for a 6kw grow. At 25 amps for the lighting, I would think that you could probably fit that plus all of your auxiliary equipment on a 60 amp panel if necessary. If you size your breaker to your existing wire, it sounds like you could easily run a 100 or 125 supply, have lots of room for future expansion and avoid the cost of larger conductors.
Okay, I see where your misunderstanding is coming from. You don't total up the amperage of the individual breakers, you have to look at what the actual load is. A 1k light on 240v is going to pull around 4.5 amps, so you can easily put 3 of them on a 20 amp breaker and still be under the 80% rule. Even if you put them behind individual breakers, you will still only be pulling 4.5 amps per light. You need to total up the actual amperage for each load and see what you get.