So I have read here. Sounds like that is the way to do things huh? Thanks for the education today you guys.
get a heatpump mini split, they will allower colder cooling operational temps, but last time i checked the AC mini splits with inverter will work to 14f, a heat pump AC will allow cooling to 0f. These numbers will change with larger BTU systems. the larger the BTU, or TONS,the colder you can run You can run a normal house AC down to -50.Most minisplit compressor systems will not operate below 50f.
No doubt, a vacuum test is kind of the opposite of a pressure test, but I didn't want to buy a bottle of N and the regulator to boot. I closed the manifold gauge and killed the pump and the needle didn't move a smidge for an hour.
I bet on simple installs, some HVAC guys skip the pressure test too. It's a gamble, I admit, but I couldn't find the fitting needed to attach the bottle of N through the manifold gauge and I was running out of time. You can't use compressed air, because it would likely contaminate the lines and make the vacuuming more difficult. Plus, you have to get the pressure up to like 400 psi to test for r410a.
It's only 25 feet of line with 4 compression fittings.
Yup a gamble it always is even when doing everything by the book you still run into troubles some times. You are also right about some hvac guys skipping this part. I have been behind some rea hack's with a HVAC license and all the tools to do it right but leave them in the truck. It don't take a lot of smarts to do hvac or I would be out of work lol. Sounds like you did just fine. You got a good vacuum and that is the most important part. Good vacuum= no leaks R.R. My reference to -20 was just a starting point . If it wont hold that there is no need to continue till you find the leak. If you continue to pull a vacuum and have a small leak you will pull moisture into the system.No doubt, a vacuum test is kind of the opposite of a pressure test, but I didn't want to buy a bottle of N and the regulator to boot. I closed the manifold gauge and killed the pump and the needle didn't move a smidge for an hour.
I bet on simple installs, some HVAC guys skip the pressure test too. It's a gamble, I admit, but I couldn't find the fitting needed to attach the bottle of N through the manifold gauge and I was running out of time. You can't use compressed air, because it would likely contaminate the lines and make the vacuuming more difficult. Plus, you have to get the pressure up to like 400 psi to test for r410a.
It's only 25 feet of line with 4 compression fittings.
Okay, I just said "fuck it" and went all out. 5.5cfm two stage pump and a digital micron gauge are on their way. I have another one of these Mr Slims to install in a few months and maybe another after that so I might as well have good tools.
What I'm wondering now is, what kind of hose do I need to connect the condenser unit with the gauge and pump? 1/4"? What kind of fittings? I really would like to get a longer hose so I could run it through my line set penetrations before I seal them up with foam and have the pump down in the basement went I draw the vacuum test. I don't need the neighbors wondering what in the hell is making all that noise, ya dig? Is this possible?
Okay, I just said "fuck it" and went all out. 5.5cfm two stage pump and a digital micron gauge are on their way. I have another one of these Mr Slims to install in a few months and maybe another after that so I might as well have good tools.
What I'm wondering now is, what kind of hose do I need to connect the condenser unit with the gauge and pump? 1/4"? What kind of fittings? I really would like to get a longer hose so I could run it through my line set penetrations before I seal them up with foam and have the pump down in the basement went I draw the vacuum test. I don't need the neighbors wondering what in the hell is making all that noise, ya dig? Is this possible?
Better go with RedRain's idea if that is your plan. Doesn't sound like a normal install. Tell the hvac guys you talk to that you want to make it portable for your hunting/fishing cabin so the thieves won't get it while your gone. When you ad or take away length to your line set you also need to add or recover freon acording to line set length..also I would bet with all the members on here there is 1 that dose hvac in your area. how to contact them idk.
I just want a long hose for the vacuum so I can use the pump inside. No changing the length of the line set here.
And I only ordered a digital gauge that reads in microns because I'm only doing the vacuum test, not pressure or anything else. Do I still need a standard gauge set if I have the micron gauge? I'm only drawing a vacuum because the unit comes pre-charged with refrigerant, correct?
Also, what do you guys think about the Viot vacuum pumps?
Excellent info in this thread. CA certified journeyman electrician here and I was planning an install very soon. Thanks to the HVAC guys for chiming in! Funny seeing people on this board that I could potentially know from some jobsite somewhere in the past...
I had a couple question for some of you with experience with these units. I have two 10x10x8 rooms with an interior wall between them. Both rooms sealed, 4kw each. I want to run a single zone in the room nearest the exterior wall and run fans between the rooms for air exchange. If I have a high volume of air exchange between the rooms and a large enough unit for both rooms, will this work? Will there be a significant temperature difference between the two rooms (both rooms will be perpetual flower)? I'd imagine the key would be, of course, proper airflow between rooms. I was thinking the single zone Mr Slim 24k btu unit. Would I just be better off getting a dual zone? Will that be enough for cooling a total of 8kw with CO2 gen and dehums.?
Also, what do you guys think about the Viot vacuum pumps? The Yellow Jackets look sweet and all but the price on the Viot pumps would be a little easier to swallow. Even if they only do the job once or twice decently before crappin out, that would be fine by me. I know I wouldn't be able to just buy one of these pumps and guage sets and call myself an AC guy but the whole procedure seems easy enough...
Any insight is totally appreciated. Thanks in advance...
Thanks guys! I think I'll look into the 3 ton units. I'd definitely rather be safe than sorry.
As far as the pumps go, I completely understand what you are saying Rain, about getting what you pay for. In my situation though, if it works once and I have to throw it away (probably won't be the case) then that's fine by me. I just really want to avoid having a tech come out to my location.
DunkyDunk, can I ask what size pump you went with off the Viot site? They have a lot of pumps and from the pictures they don't look like bad units.
I'm still up in the air about how I want to handle this, but I do have a few more weeks probably before I have to decide.
Thanks again guys...
Okay, I have everything I need except for hoses to hook up the Micron gauge and the vacuum pump. What do I ask for at the HVAC supply house? 1/4" SAE? Can I get them 10+ feet long?