I am setting up a 30 light set-up plus 25,000btu a/c, fans, pumps, and a burner. Can anyone give me advice on how to set up a sub-panel to handle this?
I think some of you guys are off on the price of the elec. I pay 3k in cali on a 20 light operation. with 5 ton ac. I pay like 7-17c a KWH =(
You're planning on running a two-room flip-flop, I assume; 15-KW's on at one time. This will be about 70-amps at 240V, with your AC being about 30-amps at 240V. Then there will be auxillary fans, inline/s, dehumidifier (7-amps @ 120V), for another 15-amps @ 120V. You're looking at about 115-amps of load; with a continuous load limit of 80%, your needs would be about 144-amps. If you have a 200-amp main service, you'll be fine. As far as the AC goes, a 5-ton, 60,000btu, split two-piece air-cooled, or, a one-piece water-cooled...nice units if you don't have metered water; check out the Thermoplus KAC-060V or Florida Heat Pump FHP-EM060, both around $3500'ish. You'll need two of everything; two burner's (ten, or larger) and a dual-zone CO2 controller, two dehum's, two charcoal scrubbers with inlines. As far as the AC, either buy two of them, or, buy/build a dual-zone motorized damper package like this:
http://www.valleyindoor.com/product.php?productid=801&cat=51&page=1
As someone has stated, assuming that you're paying for the power and not double-feeding before the meter to feed your 240V sub-panel (disclaimer: power theft is a crime, keep in mind), your bills will be $1500+/-, per month.