Ok, I think I just solved my own problem...
the wall outlets in the room are on 15a breakers, assuming the usual 14g wiring. they say don't go beyond 80% load if it is continuous, due to heat issues/fire hazards. that means a 1500w heater, running on high, is constantly pulling 12.5 amps (above 80% limit) which, in a sense, is a fire hazard and problem waiting to happen. YES it may not immediately break something, trip your breaker or cause a fire, but it is not recommended by what most electricians say.
SO, that being said,
i run 3 x 400 w ballasts during veg. in the big tent I flip out the 400's for 1000's for flowering.
right now, i could basically run all of the ballasts off the room wiring/outlets and have no problem with just 400's.
so, even when I flip to the 1000's, wouldn't it technically be safe to run a 1000W ballast on a 15a breaker? that's only 8.3A, well below the 80% threshold....so then plug the space heater into the 20A outlet that freed up?
the wall outlets in the room are on 15a breakers, assuming the usual 14g wiring. they say don't go beyond 80% load if it is continuous, due to heat issues/fire hazards. that means a 1500w heater, running on high, is constantly pulling 12.5 amps (above 80% limit) which, in a sense, is a fire hazard and problem waiting to happen. YES it may not immediately break something, trip your breaker or cause a fire, but it is not recommended by what most electricians say.
SO, that being said,
i run 3 x 400 w ballasts during veg. in the big tent I flip out the 400's for 1000's for flowering.
right now, i could basically run all of the ballasts off the room wiring/outlets and have no problem with just 400's.
so, even when I flip to the 1000's, wouldn't it technically be safe to run a 1000W ballast on a 15a breaker? that's only 8.3A, well below the 80% threshold....so then plug the space heater into the 20A outlet that freed up?