The little things add up. Boosting your yield beyond 1g/watt

There are a lot of factors to consider when you are sizing your ac for your grow. Outside temperature is a major factor to consider. The difference between summer and winter is huge. In the summer, my setup uses 3000 btu per 1000 watt, in the winter half of that. Humidity is a factor also. If it is dry, the ac runs less efficient. To give you an example of how I came up with 3000 btu per 1000 watt light, here is how mine is set up.

I find a large garage that I can build a smaller room inside the garage. Inside this room is where I grow. The Ac unit(s) blow cold air inside the grow room, while the back of the AC blows the hot air into the rest of the garage. This space that is in your garage, yet outside of your grow room, has a charcoal filter strapped to the ceiling, blowing the hot air either inside your living space (free heat in the winter) or outside the house/garage.(in the summer) If this garage area that the ac units are dumping their heat is small, or your exhaust filter is not getting rid of the heat fast enough, than the ac units will not work as efficiently.

I have seen a set up where someone custom built a box straight off the back of the AC, and inside this box, was a charcoal filter sucking the hot air to the outside. So no hot air from the AC ever escaped the custom box. He said the ac unit worked even better this way as it never tried to cool itself with the hot air it just blew out the back. I liked the idea.

The best of course is to have a split ac, where the condenser sits outside. If you want to run it in the winter you have to get a model that is made to run when it is freezing outside. I guess people would wonder why you have an AC running in the winter, but if you are running a legal(state law) grow, who cares. I have not used a split ac, but I will in the near future. It is the way to go if you are not worried about people wondering.

Hope this clarifies some questions.
Basically what I have done is convert a window unit to a split system. A window unit is a split system all housed in one box. I opened up the box and fabricated an air handler for the evap coil and use a separate fan wired into The fan control that runs the compressor and condenser coil fan. Most (maybe all) window units use the same motor to run both the blower fan and the condenser coil fan so doing this requires an additional fan. I found this to be a much cheaper alternative to using a small split system. Also, for my 2kw room even the smallest split system wouldn't run enough to pull the water out of the air and an additional dehum unit would be necessary. Perhaps if I remember I'll take a couple photos to show how I did this. It's a $99 window a/c unit, $20 worth of ducting and sheet metal and a $80 dayton blower. The trickiest part is dealing with the condensate (which I have plumbed to a drain) and avoiding kinking the refrigerant lines while fitting your air handler box around the evap coil.
As far as the moisture content of the air affecting efficiency, I think you wrote that backwards. It takes energy to pull the heat energy out of the water in the air to condense. They use more energy the more water in the air. The opposite effect can be seen in swamp coolers where the heat energy of the air is used to evaporate the the water which cools the air.
 
As far as the moisture content of the air affecting efficiency, I think you wrote that backwards. It takes energy to pull the heat energy out of the water in the air to condense. They use more energy the more water in the air. The opposite effect can be seen in swamp coolers where the heat energy of the air is used to evaporate the the water which cools the air.

Not so sure you are right about that. Seems logical what you are saying. All I know is that when the humidity is low, my ac units have a real hard time getting the temps to where I like them. As soon as the plants get big enough to transpire moisture in the air, the AC units work beautifully. Also, the water that is splashing around in the pan of the AC is there to help cool the condenser. If it is dry, there is no water to do this. I never use the condensate drain. I let the water stay in there, it is supposed to be there. My air conditioners run more efficient when it is humid. I can not explain the science behind it, but it is definitely true.
 

PoopyTeaBags

State Liscensed Care Giver/Patient, Assistant Trai
Veteran
Thanks everyone for the debate on air cooled lights. I have tried it myself only once, and found it to be a pain in the ass. I understand the concept that you can get the light closer, so more lumens on the buds, but like a previous poster said, you are making your light footprint smaller. So you are illuminating less square footage.

Has anyone tried an experiment, back to back? I would really like to know for sure what works better. Either way, I believe, getting an an air conditioner is crucial if you are running more than 4 - 1000 watts.

I have watched my friends struggle with heat problems, trying to integrate air cooled lights, plus an exhaust in the room that is always running to get rid of the heat. How do you keep your CO2 levels up if you are constantly exhausting? To me it seems like basic physics. Filter out 5% - 10% of the light, you get close to 5%-10% less results. I know you are using more electricity with an air conditioner, but I believe it pays for itself.

Maybe its hard to admit that, the sick air cooled venting system that you spent so much time putting together and spent so much money on, could have been easily replaced by an air conditioner, at half the cost and it doesn't look as cool?:yoinks:

If the debate is about which setup uses more electricity, AC of course. If the debate is about which one looks cooler, vented hoods! For me the debate is about yield per 1000 watt light. Keep in mind, the systems I am talking about are 6 - 1000 watts, or more. If you are just running 1-3 lights, the difference is irrelevant.

All i know is I haven't heard of anyone getting the yields i get, with vented hoods.(actually, vented or not) Maybe someone on ICMAG can beat my record? Is there a thread on maximum yields? I'll start one if not, I need some healthy competition. I am sure I'll find it here.

Keep the debate going!


I understand where your going with this but i beleive the lower light level makes up for the glass.... you take out the glass you raise the lights.... higher lights less lumens...i belive the glass works alot better as i aircooled and use a/c
 

Juice_Box

Member
superultramega I'm interested to know what your relative humidity is?
You said an additional dehumidifier was necessary whereas DB is trying to get the humidity up, which is a constant battle in itself when RH levels are almost always below 50%
 
I understand where your going with this but i beleive the lower light level makes up for the glass.... you take out the glass you raise the lights.... higher lights less lumens...i belive the glass works alot better as i aircooled and use a/c

One thing missing from your equation. Lower the lights, you are illuminating less square footage. You don't get more light from lowering your hoods. You get the same amount of light condensed in a smaller space. You do get less light by putting filters in front of the bulb.
 

PoopyTeaBags

State Liscensed Care Giver/Patient, Assistant Trai
Veteran
i guess it would be grow room dependent... i run alot of lights and run my lights to get as close to 60-65 watts per square foot... doing thing my lights are close together and are not dependent on putting down a huge light footprint....
 
Not so sure you are right about that. Seems logical what you are saying. All I know is that when the humidity is low, my ac units have a real hard time getting the temps to where I like them. As soon as the plants get big enough to transpire moisture in the air, the AC units work beautifully. Also, the water that is splashing around in the pan of the AC is there to help cool the condenser. If it is dry, there is no water to do this. I never use the condensate drain. I let the water stay in there, it is supposed to be there. My air conditioners run more efficient when it is humid. I can not explain the science behind it, but it is definitely true.
You're seeing that effect due to the increased respiration of your plants. The plants themselves are effectively swamp coolers. If you look into increasing home efficiency one of the first steps is to properly size the cooling unit specifically due to the increased humidity that builds up with too large a system. When the system turns on it needs to expend more energy to take that water out of the air which wastes energy. A properly sized system runs often enough to keep the humidity low. It's all about keeping the peaks and troughs of the humidity cycle as low as possible.

A/C's do not need the condensate to cool. The cooling of the compressor is achieved through the condenser coil. Mine is plumbed nearly identical to a typical split system in your house. I took a length of 1 1/2" pvc pipe and attached a cap on one end and an el on the other with a FPT bushing to attach a hose directly to a sealed drain (with trap and check valve air inlet) I took the assembled pipe and ran it through a table saw to cut the top off and turn it into a trough where the evap coil sits. All the condensate is trapped in the trough and routed to a drain.
 
superultramega I'm interested to know what your relative humidity is?
You said an additional dehumidifier was necessary whereas DB is trying to get the humidity up, which is a constant battle in itself when RH levels are almost always below 50%
It's right at about 50% I actually do have a dehum in the room hooked up to a humidistat, but it only tends to run late in flowering when the lights are off (and the a/c is obviously not running).
All that water you're losing from your res is coming through the plants into the air. That's a lot of water in the air! Any problems with low RH could be traced to an a/c that runs too often (too small) or ventilating with very low RH air (sucking out the moist air and replacing it with very dry air. Or both.
 
You're seeing that effect due to the increased respiration of your plants. The plants themselves are effectively swamp coolers. If you look into increasing home efficiency one of the first steps is to properly size the cooling unit specifically due to the increased humidity that builds up with too large a system. When the system turns on it needs to expend more energy to take that water out of the air which wastes energy. A properly sized system runs often enough to keep the humidity low. It's all about keeping the peaks and troughs of the humidity cycle as low as possible.

A/C's do not need the condensate to cool. The cooling of the compressor is achieved through the condenser coil. Mine is plumbed nearly identical to a typical split system in your house. I took a length of 1 1/2" pvc pipe and attached a cap on one end and an el on the other with a FPT bushing to attach a hose directly to a sealed drain (with trap and check valve air inlet) I took the assembled pipe and ran it through a table saw to cut the top off and turn it into a trough where the evap coil sits. All the condensate is trapped in the trough and routed to a drain.

That is something I never considered. The plants themselves, acting as swamp coolers. Thanks for bringing that up. I dig it.

As far as the ac's not needing the water in the pan, to cool itself, I am aware of that. It does help though. In the manual for the ac it says that is what it is there for. The pan is designed to fill with water to a certain level, so the fan splashes it up on the condenser fins. You probably already knew that though.

You bring up some interesting points about the humidity effecting efficiency. I'll have to think about that more.
 
That is something I never considered. The plants themselves, acting as swamp coolers. Thanks for bringing that up. I dig it.

As far as the ac's not needing the water in the pan, to cool itself, I am aware of that. It does help though. In the manual for the ac it says that is what it is there for. The pan is designed to fill with water to a certain level, so the fan splashes it up on the condenser fins. You probably already knew that though.

You bring up some interesting points about the humidity effecting efficiency. I'll have to think about that more.
Yeah that would certainly help as it would assist the condenser coil by adding some swamp cooling to the air cooling of the condenser coil. Mine seems to run efficiently enough as my elec usage is pennies on the dollar compared to yields. If you're in a situation where leaving that condensate is ok (not my situation) that would definitely help efficiency of your unit.
 

funkfingers

Long haired country boy
Veteran
I would agree with most things that you have listed, however I would add one. Using a screen of green setup can greatly increase your yield
by evening out the canopy, and virtually eliminating lower shelf buds, I have seen 1st hand how beneficial this method of growing is to your yield.
 

VerdantGreen

Genetics Facilitator
Boutique Breeder
Mentor
ICMag Donor
Veteran
true funkyfingers, and the same could be said about scrog. its all about having all your buds the ideal distance from the light with as few gaps as possible

V.
 

delta9nxs

No Jive Productions
Veteran
the btu figure i gave is from one of my old books, rosenthal or cervantes or somebody. but i have found that to be a good rough rule of thumb as a 1k burns more than 1k juice in operation. every room is different. outside ambient temps are a major factor. insulation is a priority. if i ever get a chance to build a room from scratch it will be super insulated, i'm talking R 30-40 minimum. i will also run a mini-split.

light loss through the glass of a cool tube is around 10%, not 33%. look at the greenhouse industry for verification. using the inverse square rule, where each foot of distance away from the light is 4 times weaker than the previous foot, my 8" from the closest foliage is 332% the effective light at 16", with or without cooltubes. all my plants are in the sweet spot of the lights. a 1k hps at 16" is equal to the tropical noonday sun.

vertical light orientation is vastly more efficient than horizontal. i will include a graphic from our old friend krusty as well as a photo of my flower area. my room is only 6.5' wide and i grow large plants. i ran the same ballasts and bulbs horizontal in the same room with non-cooled reflectors. my lights on temps are now 75-80F at all times.

i have run sog e&f in the same space with the same lights and got about the same yield but did a hell of a lot more work to get there. large plants numbers and constant light adjustment. now i have no more than 20 plants at any given time.

also, no one has mentioned the effect of strain on yield. i've only grown out about 30 or so strains but i know i got radically different yields from them. btw, what strain are you running?

oh well, i just thought i'd throw in a little more fuel for thought. later
 
Last edited:

chef

Gene Mangler
Veteran
My 12k btu AC cools 4kw of open bulbs on low in the summer, 10x10 room.
I keep it 77-82 & aprox 40rh.
My dehumidifier is also pulling 7+ gals a day from 18 plants.
Thats when you know they're kickin ass ;)

I'm in soil, so an underdog in this forum :)
 

jmansweed

Member
Great thread. Effeciency on all fronts is the key to making your numbers climb consistantly. I've used both air-cooled lights w/ air conditioning and "open" lights in the air conditioning. I yeilding more with the air-cooled system probably because I could get more lumens closer to the plants. I use soiless all organic, and have for years. After breeding Big Bud with Green Spiret, and crossing in NYCD I developed a strain that produced 1.4 gpw - the bud turned out of less quality than I had hoped but still was very respectable. In any case props if your consistantly spitting out 1 or 2 gpw - that's a fantastic avg. I always run the air-cooled lights w/ an air conditioner these days but might try removing the lense on a few and checking the #'s again......peace
 

chef

Gene Mangler
Veteran
It'll take CO2 to put me over 1gpw, pulling the highest yield per SgFt I have in over 30yrs tho. 1.3+ in <90 days & still climbing ;) Thats with homespun genetics, running some BOG & DJ real soon, will give me some #'s to cross reference against other grows.

This thread is spot on that the little things are what truly make a difference.
There are no silver bullets, but fill your quiver with little tricks & kaboom! ;)
 