bobs your uncle
Member
I have three phase power separately metered from my main single phase service at my workshop. The three phase is 3 wire and is dedicated to one motor/hoist. I don't know if the transformer is a delta or wye, but I'm assuming it's a delta. There is no neutral. The disconnect for the three phase says "220v 3ø" although my meter reads about 208v between any of the three phase conductors. I didn't detect a "high leg" or "b" phase conductor if that helps. It's an older building, all three conductors are black.
Can I use two of the conductors in a "line -to- line" connection to supply a 208v single phase load, and if so, how do I distribute the load evenly across the phases to keep the system balanced? I know I can't derive 120v single phase as there is no neutral.
cocktail frank? Pharma? you out there?
Can I use two of the conductors in a "line -to- line" connection to supply a 208v single phase load, and if so, how do I distribute the load evenly across the phases to keep the system balanced? I know I can't derive 120v single phase as there is no neutral.