i need to put in a new 240v circuit to run my new room. im learning up on it before i do it. but the little things have me confused...

heres one:


i bought an "Intermatic T104" timer board, which is already wired up to the needed 240v outlets, so thats taken care of. I just need to hardwire it to my new 240v circuit when i drop it in. What I'm confused about is, do I absolutely need to run this on a 40amp circuit? I got a bit confused, and I thought the guy at the hydro store told me to buy a double pole 30amp 240v breaker. I'm only pulling 10 amps + fans on 240v so 30amps is fine for that application, but why wouldn't he tell me to put in a 40amp circuit and breaker instead? Maybe I got confused and he really did say 40amp... on top of that he gave me the correct wire to run from the main panel to be hard-wired into my wh40, so whatever gauge he gave me is correct for either one of 30amp or 40 amp, i can't remember and i don't have it on hand with me ATM and the shops closed.

either way, what would happen if I put in a 30amp circuit and breaker and wired it up to the t104 timer, made for 40amps? and, if he did in fact tell me to put in a 30amp circuit and NOT 40amps, what would the reason for this be?

i have no reason not to run 40amps . as far as i know it just allows me greater expansion room as long as i keep in mind the total draw of the house.

i'll get this all sorted tomorrow when the shops open but id personally just like to know , as im trying to learn as much as i can. i have a feeling i just messed up and im really supposed to run 40amps and i just got the wrong breaker by mistake.

thanks
 
S

sparkjumper

The timer is rated for 40A max,that doesnt mean you need to feed it with 8 wire for a 40A circuit or even 10 wire for a 30A circuit,it's just a maximum rating for the device.The branch circuit wiresize should determine your breaker size.If you are feeding the timer with #10AWG then a 2 pole 30 is what you want.You can undersize a breaker but you cant oversize.You can put a 2 pole 20 on a 10 wire circuit but you cant put a 2 pole 30 on a 12 wire circuit if that makes any sense.Basically you want 30A for 10 wire 20A for 12 wire and 15A for 14 wire
 
The timer is rated for 40A max,that doesnt mean you need to feed it with 8 wire for a 40A circuit or even 10 wire for a 30A circuit,it's just a maximum rating for the device.The branch circuit wiresize should determine your breaker size.If you are feeding the timer with #10AWG then a 2 pole 30 is what you want.You can undersize a breaker but you cant oversize.You can put a 2 pole 20 on a 10 wire circuit but you cant put a 2 pole 30 on a 12 wire circuit if that makes any sense.Basically you want 30A for 10 wire 20A for 12 wire and 15A for 14 wire

ok cool, so i have to make sure i have a have a big enough wire from the breaker feeding my timer to handle either 30 or 40 amp loads. im gonna get a 40 amp breaker and make sure i have the correct #8 wiring. if im doing it already i see no reason why i shouldnt just go for 40


thanks
 
S

sparkjumper

Unless you are doing a huge grow bro that really is overkill.You say you are only pulling 10 amps plus a few fans?240V fans?Anyway 10 wire on a 30A breaker would give you plent of room for expansion as you can safely go 24 amps on a 10 wire 30A circuit.You dont want to mess with 8 wire bro unless the load demands it
 
Unless you are doing a huge grow bro that really is overkill.You say you are only pulling 10 amps plus a few fans?240V fans?Anyway 10 wire on a 30A breaker would give you plent of room for expansion as you can safely go 24 amps on a 10 wire 30A circuit.You dont want to mess with 8 wire bro unless the load demands it


alright man, thats the feeling i got. the 8 wire is hella thick and i think ill have serious problems getting it hardwired into the box. im running 3- 120v fans but they are being run on the same circuit / timer on the 120v receptacles. and then an A/C for summer on its own 120v circuit. so thats under 24 amps. thanks for the info i guess its back to the store for a 30 amp breaker.
 