Hey guys, its getting close to the end of the outdoor season, and my mediocre outdoor this year is extremely subpar. I'm hoping to have my indoor room ready to flip early/mid November, so I'm trying to get the ball rolling right now, and hopefully have a nice grow journal for you guys towards the end of the year.
I had an electrician come out and put a subpanel in our 12 ' x 12 ' shed(100 feet from the home). Homes on a 100amp main, we tapped into an unused 50a 240v breaker and brought it out to the shed (8 gauge thhn wire 90degree C, I believe, is rated for up to 55 amps at 100 feet?). If necessary, I can buy a 55 amp breaker and replace the 50 amp, I'm not sure how necessary this will be.
The subpanel has a 50 amp 240v breaker on an intermatic timer, with 5 or 6 240v plugs. The sub panel also has a 20 amp 120v breaker, with a few plugs as well. Even though I have 70 amps of breakers, I can't pull more than 50 amps (or 40 amps continuous power?).
What I would LIKE to do, is run 5KW bloom with a 24k-36k btu minisplit. A harvest or two down the line, if things go well, I would like to upgrade the homes main panel, run another 50 amps to the sheds subpanel, and do a 8kw or 9kw sealed bloom room.
Is it possible for me to put a 24k or 36k btu ac safely on the same 50a breaker as the 5kw of lights? On the 120 circuit we'd only have a few oscillating fans, a pond fogger, and co2 gen.
-if it was on the same 240v breaker, the ac would be on the same 12 hour cycle as the HIDs.
-I'd really prefer to install a 36k btu, so I could chose to run bare bulbs, omitting the need for any inline fans and holes in walls that need to be blacked out, and allow me to upgrade to 8 lights as long as I exhausted my hoods at that point.
- 5 ballasts/bulbs @ 4.5 amps each = 22.5
- 36k btu ac, max amp draw is 17.8 amps
------------------------------------------------------
40.3 amps, only 22.5 of which are continuous power
This would technically leave around ten amps for 120 v appliances, correct?
Seems reasonable to me, but am I missing something?
I had an electrician come out and put a subpanel in our 12 ' x 12 ' shed(100 feet from the home). Homes on a 100amp main, we tapped into an unused 50a 240v breaker and brought it out to the shed (8 gauge thhn wire 90degree C, I believe, is rated for up to 55 amps at 100 feet?). If necessary, I can buy a 55 amp breaker and replace the 50 amp, I'm not sure how necessary this will be.
The subpanel has a 50 amp 240v breaker on an intermatic timer, with 5 or 6 240v plugs. The sub panel also has a 20 amp 120v breaker, with a few plugs as well. Even though I have 70 amps of breakers, I can't pull more than 50 amps (or 40 amps continuous power?).
What I would LIKE to do, is run 5KW bloom with a 24k-36k btu minisplit. A harvest or two down the line, if things go well, I would like to upgrade the homes main panel, run another 50 amps to the sheds subpanel, and do a 8kw or 9kw sealed bloom room.
Is it possible for me to put a 24k or 36k btu ac safely on the same 50a breaker as the 5kw of lights? On the 120 circuit we'd only have a few oscillating fans, a pond fogger, and co2 gen.
-if it was on the same 240v breaker, the ac would be on the same 12 hour cycle as the HIDs.
-I'd really prefer to install a 36k btu, so I could chose to run bare bulbs, omitting the need for any inline fans and holes in walls that need to be blacked out, and allow me to upgrade to 8 lights as long as I exhausted my hoods at that point.
- 5 ballasts/bulbs @ 4.5 amps each = 22.5
- 36k btu ac, max amp draw is 17.8 amps
------------------------------------------------------
40.3 amps, only 22.5 of which are continuous power
This would technically leave around ten amps for 120 v appliances, correct?
Seems reasonable to me, but am I missing something?