New member
I know that 1000w = 3412 BTU, so theoretically the bulb itself, being fed 1000w, will put out 3412BTU.
But then you have the ballast...where I've seen quotes from as low as 1500BTU for digitals, to as high as 4000BTU for magnetic.
This is where I'm confused. When I checked my ballasts input current (quantum digital), each one was pulling about 1060w total...so 1000w was going to the bulb, and 60w was "lost" (as heat, obviously, due to inefficiency).
So, if the ballast and bulb combination as a whole is pulling in 1060w TOTAL, and we already have 3412BTU for the bulb, how is that extra 60w producing 1500-4000BTU of heat???????????
The way I see it, that extra 60w is only capable of creating 204BTU (60*3.412) of heat, nowhere near the 1500-4000 I've seen mentioned.
In order for the ballasts to create, lets say an average, of 1750BTU, that would take 512watts to make.....so 512 watts for the ballast, added to the 1000w for the bulb, gives us each ballast/bulb combo pulling 1512w....which I know mine and many others I've measured definitely don't, as that would be less than 50% efficient.
I've seen one guy say ballasts have a "heat leakage" of 2.5BTU/watt, but I have no idea what that even means....you can't make heat from nothing....and as I said, the ballasts are only using/shedding an extra 60w over the 1000w for the bulb, so I can't see where all that heat is coming from.
This all started when I tested a new sealed start-up room with 6000w of uncooled HID (20,472BTU) and also the ballasts in the room as well (supposedly another 10,500 BTU using the 1750/ballast figure), putting total BTU at 30,972.......the 24000BTU AC had no issue at all cooling the room, in fact, it only ran at about 90% (inverter unit), indicating the BTU load was actually around 21,700, which closely matches the BTU calc for 6 1060w ballast/bulb combos. If the ballasts had been putting out the rumored 1750btu, the 24k AC would not have been able to keep up at all.
Can anyone shed some light on this "heat leakage" thing, and how the ballasts are supposedly putting out so much heat, while only losing 60w from inefficiency?
But then you have the ballast...where I've seen quotes from as low as 1500BTU for digitals, to as high as 4000BTU for magnetic.
This is where I'm confused. When I checked my ballasts input current (quantum digital), each one was pulling about 1060w total...so 1000w was going to the bulb, and 60w was "lost" (as heat, obviously, due to inefficiency).
So, if the ballast and bulb combination as a whole is pulling in 1060w TOTAL, and we already have 3412BTU for the bulb, how is that extra 60w producing 1500-4000BTU of heat???????????
The way I see it, that extra 60w is only capable of creating 204BTU (60*3.412) of heat, nowhere near the 1500-4000 I've seen mentioned.
In order for the ballasts to create, lets say an average, of 1750BTU, that would take 512watts to make.....so 512 watts for the ballast, added to the 1000w for the bulb, gives us each ballast/bulb combo pulling 1512w....which I know mine and many others I've measured definitely don't, as that would be less than 50% efficient.
I've seen one guy say ballasts have a "heat leakage" of 2.5BTU/watt, but I have no idea what that even means....you can't make heat from nothing....and as I said, the ballasts are only using/shedding an extra 60w over the 1000w for the bulb, so I can't see where all that heat is coming from.
This all started when I tested a new sealed start-up room with 6000w of uncooled HID (20,472BTU) and also the ballasts in the room as well (supposedly another 10,500 BTU using the 1750/ballast figure), putting total BTU at 30,972.......the 24000BTU AC had no issue at all cooling the room, in fact, it only ran at about 90% (inverter unit), indicating the BTU load was actually around 21,700, which closely matches the BTU calc for 6 1060w ballast/bulb combos. If the ballasts had been putting out the rumored 1750btu, the 24k AC would not have been able to keep up at all.
Can anyone shed some light on this "heat leakage" thing, and how the ballasts are supposedly putting out so much heat, while only losing 60w from inefficiency?