Burnt up neutral wire (causes)???

mowood3479

Active member
Veteran
A few weeks back I had a neutral wire burn up (from where it entered the neutral bar n back 2-3 inches..)
120v 20amp circuit.. With mayb 6 Amps in fans and a small Dehuey 5 amps.
I clipped off the burnt section of 12/2 Romex and put the neutral wire into a new spot on the nuetral bar and it's worked fine the last two weeks.
Just wondering why it could've happened in the first place.
I read in another thread it's possibly a faulty breaker?
Should I replace the breaker asap? Not sure what the heck happened.
Any theories would be welcomed.
Thx
 

mowood3479

Active member
Veteran
Also this never tripped the breaker... I couldn't figure out what was wrong at first because the circuit was testing that it was live.. But none of the equip on the circuit would work.
Seems strange to me.
 

HidingInTheHaze

Active member
Veteran
My guess is a loose connection.

Breakers trip when there is A. an overload or B. a dead short (when hot and neutral, or hot and ground come in contact)

With a loose connection, the wire just arcs, creating heat until it eventually burns up.
 

theother

Member
A few weeks back I had a neutral wire burn up (from where it entered the neutral bar n back 2-3 inches..)
120v 20amp circuit.. With mayb 6 Amps in fans and a small Dehuey 5 amps.
I clipped off the burnt section of 12/2 Romex and put the neutral wire into a new spot on the nuetral bar and it's worked fine the last two weeks.
Just wondering why it could've happened in the first place.
I read in another thread it's possibly a faulty breaker?
Should I replace the breaker asap? Not sure what the heck happened.
Any theories would be welcomed.
Thx

Pm rives and out him to the thread, that's probably your best bet.
 

nukklehead

Active member
My guess is a loose connection.

Breakers trip when there is A. an overload or B. a dead short (when hot and neutral, or hot and ground come in contact)

With a loose connection, the wire just arcs, creating heat until it eventually burns up.



Im no rives but haze nailed it.. have had loose wires before.. same thing..
 

rives

Inveterate Tinkerer
Mentor
ICMag Donor
Veteran
Yep, Haze is correct on all counts. As he said, standard breakers are only good for sustained overloads or direct shorts, a GFCI adds the function of sensing low level faults to ground and AFCI's add arc protection. A loose connection should have been picked up by an AFCI, but the other breakers will happily ignore it.
 