I'm hooking up a 240volt a/c... so from the panel I have a 40a 2pole breaker...
I know I have to use #8 for this.. now my Q is;..
can I run the #8 to a J box from the panel, then from the j box to the a/c use #10??...
the a/c only pulls 9.9amps.. I plan on running some lights 240 off of the same 40a breaker...
thanks for the help...