Running a little low on poles within this sub panel. Wanted to double check, get a little consensus if this wiring sounds right. The goal is to plug in 4x 220v 1kw lights.
30 amp dual pole breaker. Romex 10-2 from breaker into a junction box , 2 runs of Romex 12-2 pig tailed to the 10-2 in the junction box. Each lead of 12-2 will lead to a 20a duplex 220v outlet.
Could do the pig tailing within a double gang box, but I feel like using a junction box would be cleaner, less crammed, easier access to the connection.
Anyone notice anything wrong with this set up?
Thanks,
Mr^^
Yep. Your breaker is too large to protect the downstream components. The breaker needs to be sized at or below the lowest-rated component in the circuit.
You might consider running the feed from your panel into a small sub-panel and distributing your 15a or 20a circuits out of it. This won't cost you any more space in your main panel and will give you the downstream protection that you need. Small subs can be had for under $20.